I have a Enviromon system EL005 with EL026 and EL006.
I programed the system to collect data from 15 in 15 minutes and the alarm to active after 1 minute, but it only activates after the time that is programmed to collect, 15 in 15 minutes, this is correct or there is really a failure the system.
The system never alarm after 1 minute when the temperature exit the parameters set for maximum and minimum, what should I do?
Enviromon
Hi the alarm will only happen after the average sample over your sampling period falls in the alarm condition. So if you had a sampling period of 15 mins, you would have to wait at least 15 mins. I would recommend sampling at 1 min intervals really in that way the alarm condition would take 1 or 2 mins.
Kind regards
Kind regards
Ziko
Technical Specialist
Technical Specialist