Test and Measurement Forum



Postby laerte » Sat Feb 28, 2009 4:55 pm

I have a Enviromon system EL005 with EL026 and EL006.
I programed the system to collect data from 15 in 15 minutes and the alarm to active after 1 minute, but it only activates after the time that is programmed to collect, 15 in 15 minutes, this is correct or there is really a failure the system.
The system never alarm after 1 minute when the temperature exit the parameters set for maximum and minimum, what should I do?
Posts: 1
Joined: Sat Feb 28, 2009 4:44 pm

Postby ziko » Tue Mar 03, 2009 4:56 pm

Hi the alarm will only happen after the average sample over your sampling period falls in the alarm condition. So if you had a sampling period of 15 mins, you would have to wait at least 15 mins. I would recommend sampling at 1 min intervals really in that way the alarm condition would take 1 or 2 mins.

Kind regards

Technical Specialist
Zen Master
Zen Master
Posts: 1705
Joined: Fri Dec 01, 2006 10:03 am
Location: St Neots

Return to Software

Who is online

Users browsing this forum: No registered users and 0 guests