Test and Measurement Forum

Physical Alarms with the enviromon

Physical Alarms with the enviromon

Postby hjcrooks » Mon Nov 29, 2004 2:35 pm

Just want to know is it possible to have alarm outputs from the enviromon to allow a warning sounder to be activated if the temperature in a freezer strays out of limits? Ideally it should only sound if the alarm condition remains for a pre-determined period of time i.e. 60 minutes.

Best regards

Jim Crooks

Postby Sarah » Wed Dec 01, 2004 12:15 pm

Hi Jim

Thank you for your post.

Yes, it is possible to have an alarm sound in the conditions that you describe. The external alarm is the EL006 and the software will enable you to set this so that if a parameter goes out of range it will sound. You can set a delay so that it will only go off if the parameter remains out of range for a specified period of time.

Hope this helps

Best Regards

Return to Hardware

Who is online

Users browsing this forum: No registered users and 0 guests