Alarm with green button

Post by Laven »

Hi,

I had a problem with the Enviromon system. Some buttons were green when alarming. I had made an update of the configuration without turning off all sounding alarms so I suspected that it was the problem. So I reseted all configuration and started all over again. That worked fine, but after a while the system freezed so I had to restart it. Now I have the same problem again. I had saved the configuration before the crash but when I load it up I have the same problem.
I don't want to start from scratch again because it's a lot of configuring. Is there another way to make it work?
anlav

ziko
Advanced User
Advanced User
Posts: 1705
Joined: Fri Dec 01, 2006 10:03 am
Location: St Neots

Re: Alarm with green button

Post by ziko »

Hi could you send me your ini file? this is located by default in the following location:

C:\Program Files\Pico Technology\EnviroMon\

Regards
Ziko

Technical Specialist

Laven
User
User
Posts: 2
Joined: Thu Oct 09, 2008 6:38 am

Re: Alarm with green button

Post by Laven »

ziko wrote:Hi could you send me your ini file? this is located by default in the following location:

C:\Program Files\Pico Technology\EnviroMon\

Regards
Hello Zeke,
There is an autodialer connected to the system and it works alright, just as information.

Here is the text in the ini-file:

Code: Select all

[Logger1]
Connection=0
Port=1
BaudRate=57600
Address=1
Telephone=
AlarmTel=
AlarmConn=0
AlarmRepeat=0
UnitIdentifier=
Server=
AnswerStart=0
AnswerEnd=0
Printer=0
PrintCurrent=No
PrintSummary=No
CurrentMinutes=60
SummaryMinutes=1440
DialerPresent=No
MainsFailMinutes=5
NetFailMinutes=5
PowerSampling=0
PowerSerial=0
NoOfConverters=5
SoftwareVersion=26
HardwareVersion=5
[Logger1, Converter1]
Address=1
Type=129
[Logger1, Converter2]
Address=3
Type=9
[Logger1, Converter3]
Address=7
Type=9
[Logger1, Converter4]
Address=10
Type=9
[Logger1, Converter5]
Address=11
Type=2
[General]
NoOfLoggers=1
NoOfSensors=15
Configured=Yes
Release=R5.21.5 - 32 bit
Application=EMW
StartMode=0
MinutesPerReading=1
SampleMode=0
MaxReadings=1000
Session=0
DataPath=C:\Program Files\Pico Technology\EnviroMon\
BackupPath=e:\
AutoBackup=No
DeleteAfter=0
NoOfGroups=4
[Sensor1]
Logger=1
Converter=11
Channel=3
Active=Yes
ConverterType=2
Conditioner=0
Type=1
AlarmEnabled=0
Minimum=-32752
Maximum=32752
Holdoff=0
Hysteresis=50
AlarmOutputs=0
Units=°C
Name=B16 45°C Flaskbad  T168
[Sensor2]
Logger=1
Converter=11
Channel=2
Active=Yes
ConverterType=2
Conditioner=0
Type=1
AlarmEnabled=0
Minimum=-32752
Maximum=32752
Holdoff=0
Hysteresis=50
AlarmOutputs=0
Units=°C
Name=B7 45°C Dilumatbad  T167
[Sensor3]
Logger=1
Converter=11
Channel=1
Active=Yes
ConverterType=2
Conditioner=0
Type=1
AlarmEnabled=0
Minimum=-32752
Maximum=32752
Holdoff=0
Hysteresis=50
AlarmOutputs=0
Units=°C
Name=B1 45°C Substratbad T166
[Sensor4]
Logger=1
Converter=10
Channel=4
Active=No
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=0
Minimum=-32752
Maximum=32752
Holdoff=0
Hysteresis=50
AlarmOutputs=0
Units=°C
Name=4: 
[Sensor5]
Logger=1
Converter=10
Channel=3
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=28
Maximum=108
Holdoff=10
Hysteresis=2
AlarmOutputs=4
Units=°C
Name=A8 5,8°C  T151
[Sensor6]
Logger=1
Converter=10
Channel=2
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=47
Maximum=107
Holdoff=10
Hysteresis=2
AlarmOutputs=8
Units=°C
Name=A20 7,7°C  T148
[Sensor7]
Logger=1
Converter=10
Channel=1
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=49
Maximum=109
Holdoff=10
Hysteresis=2
AlarmOutputs=8
Units=°C
Name=A19 7,9°C  T147
[Sensor8]
Logger=1
Converter=7
Channel=4
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=47
Maximum=107
Holdoff=10
Hysteresis=2
AlarmOutputs=8
Units=°C
Name=A24 7,7°C  T115
[Sensor9]
Logger=1
Converter=7
Channel=3
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=47
Maximum=107
Holdoff=10
Hysteresis=2
AlarmOutputs=8
Units=°C
Name=A23 7.7°C  T149
[Sensor10]
Logger=1
Converter=7
Channel=2
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=107
Maximum=167
Holdoff=10
Hysteresis=2
AlarmOutputs=8
Units=°C
Name=A22 13,7°C  T150
[Sensor11]
Logger=1
Converter=7
Channel=1
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=18
Maximum=78
Holdoff=10
Hysteresis=2
AlarmOutputs=8
Units=°C
Name=A21 4.8°C  T116
[Sensor12]
Logger=1
Converter=3
Channel=4
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=26
Maximum=86
Holdoff=10
Hysteresis=2
AlarmOutputs=2
Units=°C
Name=A39 4.6°C  T112
[Sensor13]
Logger=1
Converter=3
Channel=3
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=54
Maximum=94
Holdoff=10
Hysteresis=2
AlarmOutputs=2
Units=°C
Name=A31 7.4°C  T165
[Sensor14]
Logger=1
Converter=3
Channel=2
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=49
Maximum=119
Holdoff=10
Hysteresis=2
AlarmOutputs=4
Units=°C
Name=A10 7.9°C  T164
[Sensor15]
Logger=1
Converter=3
Channel=1
Active=Yes
ConverterType=9
Conditioner=0
Type=34
AlarmEnabled=1
Minimum=52
Maximum=112
Holdoff=10
Hysteresis=2
AlarmOutputs=4
Units=°C
Name=A9 8,2°C  T163
[Monitor1]
Autosave=No
NoOfChannels=14
Channel1=1
Channel2=2
Channel3=3
Channel4=5
Channel5=6
Channel6=7
Channel7=8
Channel8=9
Channel9=10
Channel10=11
Channel11=12
Channel12=13
Channel13=14
Channel14=15
Channel15=15
[Holdoff]
NoOfHoldoffs=9
Sensor0=4
Count0=10
Sensor1=5
Count1=10
Sensor2=6
Count2=10
Sensor3=7
Count3=10
Sensor4=8
Count4=10
Sensor5=9
Count5=10
Sensor6=10
Count6=10
Sensor7=11
Count7=10
Sensor8=13
Count8=10
[Preferences]
BeepOnReading=No
BeepOnLamp=Yes
BeepOnAlarm=Yes
[MonitorDisplay]
Logger1=1
[AlarmMessages]
AlarmMessage0=
AlarmMessage1=
AlarmMessage2=
AlarmMessage3=
AlarmMessage4=
[Temperature]
Fahrenheit=No
DecimalPlaces=2
SysMaximum=32700
SysMinimum=-32700
[Alarm]
Hysteresis=20
Latch=No
Repeat=20
[Site]
Name=
Maintenance=
[Events]
NoOfActive=11
Active1=87
Active2=60
Active3=40
Active4=41
Active5=39
Active6=43
Active7=72
Active8=91
Active9=19
Active10=32
Active11=21
[Group 1]
Member1=5
Member2=6
Member3=7
Member4=8
Member5=9
Member6=10
Member7=11
Member8=12
Member9=13
Member10=14
Member11=15
Name=Kyl
NoOfMembers=11
[Group 2]
Member1=6
Member2=7
Member3=8
Member4=9
Member5=10
Member6=11
Name=Sensorik
NoOfMembers=6
[Spread1]
Filename=C:\Program Files\Pico Technology\EnviroMon\20120601.prn
Start=17058506
Col=4
NoOfSensors=15
Sensor1=1
Sensor2=2
Sensor3=3
Sensor4=4
Sensor5=5
Sensor6=6
Sensor7=7
Sensor8=8
Sensor9=9
Sensor10=10
Sensor11=11
Sensor12=12
Sensor13=13
Sensor14=14
Sensor15=15
Autosave=Yes
Individual=Yes
First=No
Average=No
Maximum=No
Minimum=No
MinutesPerRow=1
ScrollRange=2
[Graph1]
Start=17055360
End=17056799
NoOfFrames=1
MinValue1=3.165000
MaxValue1=8.335000
MinDefaultValue1=0.000000
MaxDefaultValue1=1000.000000
Duration=24
Autoscale=Yes
Autosave=Yes
Markers=Yes
Format=0
Title=
NoOfChannels=1
Channel1=12
[Group 3]
Member1=12
Member2=13
Name=Korridor
NoOfMembers=2
[Group 4]
Member1=5
Member2=14
Member3=15
Name=Kylrum
NoOfMembers=3
Best regards. Anders Lavén, Arla Foods
anlav

ziko
Advanced User
Advanced User
Posts: 1705
Joined: Fri Dec 01, 2006 10:03 am
Location: St Neots

Re: Alarm with green button

Post by ziko »

I noticed that you have a hold off for 10 mins, could you send your archive file to me at support@picotech.com. So save your configuration as an archive so I an look at the data.

Settings-> Configuration -> Save As Archive.
Cheers
Ziko

Technical Specialist

Laven
User
User
Posts: 2
Joined: Thu Oct 09, 2008 6:38 am

Re: Alarm with green button

Post by Laven »

Thank You for your reply:
"Hi I have managed to recreate your problem, this seems to be a problem with refreshing the display.  I noticed that if you go into Settings->Monitors-> Channels and then click on exit it updates the display.  The device works perfectly fine its jut the monitor view is not being update.

I iwll forward this to the software engineers.

Kind regards

Ziko"

I've tested it now and it works perfectly. This is a good way to make it work for me. Thanks a lot!
anlav

ziko
Advanced User
Advanced User
Posts: 1705
Joined: Fri Dec 01, 2006 10:03 am
Location: St Neots

Re: Alarm with green button

Post by ziko »

No problem, took a bit of testing to see what was the problem!
Ziko

Technical Specialist

Laven
User
User
Posts: 2
Joined: Thu Oct 09, 2008 6:38 am

Re: Alarm with green button

Post by Laven »

Hi again!

It's been some time now and I'm wondering if something happens about the software update.
It's still a bit annoying that you have to update the list to see the alarms and there has been some misunderstandings because of that. You have to wait until the temerature is ok before you update it if you don't want to have an alarm inspite that everything is alright.
anlav

ziko
Advanced User
Advanced User
Posts: 1705
Joined: Fri Dec 01, 2006 10:03 am
Location: St Neots

Re: Alarm with green button

Post by ziko »

Hi Laven,

Unfortunately no modifications have been made so far, EnviroMon goes through very few modifications. Usually if something big is added or fixed.

Regards
Ziko

Technical Specialist

Laven
User
User
Posts: 2
Joined: Thu Oct 09, 2008 6:38 am

Re: Alarm with green button

Post by Laven »

I think I've found the problem. Senor number 4 was disabled. Sensor 1-3 worked alright but 5-12 didn't change colour. When I enabled sensor 4 and sent the information to the loggers, sensor 5-12 worked normally again. :)